November 24th, 2002, 09:36 PM
#1
Inactive Member
I need a little help in sizing an x-mer.
600v mains droped down to 208 /120v
50A welder recpt
8x20A recpt
30A trailer
15A lighting
the first 4 loads will be out of 1 panel and i would like the avaibility of 50 to 100 amps for future use.
thanks
-
November 25th, 2002, 03:35 AM
#2
HB Forum Owner
Could use a little more information, but here goes anyway.
Assuming -
- the welder is 208 volt, 1 phase
- the receptacles are all 120 volt
- the trailer is 120 volt
- your future 100 amps will be 120 volt loads
Welder = 10400 va
Recepts = 19200 va
Trailer = 3600 va
Lighting= 1800 va
Future = 6228 va
Total = 41228 va = 41.2 kva - with everything on at once.
With normal use, 25 or 30 kva should do it.
Ed
-
November 25th, 2002, 03:52 AM
#3
Inactive Member
<BLOCKQUOTE><font size=2 face="Verdana, Helvetica, sans-serif">quote:</font><table border="0" width="90%" bgcolor="#333333" cellspacing="1" cellpadding="0"><tr><td width="100%"><table border="0" width="100%" cellspacing="0" cellpadding="2" bgcolor="#FF9900"><tr><td width="100%" bgcolor=""><font size=2 face="Verdana, Helvetica, sans-serif">Originally posted by electric-ed:
Could use a little more information, but here goes anyway.
Assuming -
- the welder is 208 volt, 1 phase
- the receptacles are all 120 volt
- the trailer is 120 volt
- your future 100 amps will be 120 volt loads
Welder = 10400 va
Recepts = 19200 va
Trailer = 3600 va
Lighting= 1800 va
Future = 6228 va
Total = 41228 va = 41.2 kva - with everything on at once.
With normal use, 25 or 30 kva should do it.
Ed</font></td></tr></table></td></tr></table></BLOCKQUOTE>
-
November 25th, 2002, 03:59 AM
#4
Inactive Member